Skip to content
×
Try PRO Free Today!
BiggerPockets Pro offers you a comprehensive suite of tools and resources
Market and Deal Finder Tools
Deal Analysis Calculators
Property Management Software
Exclusive discounts to Home Depot, RentRedi, and more
$0
7 days free
$828/yr or $69/mo when billed monthly.
$390/yr or $32.5/mo when billed annually.
7 days free. Cancel anytime.
Already a Pro Member? Sign in here

Join Over 3 Million Real Estate Investors

Create a free BiggerPockets account to comment, participate, and connect with over 3 million real estate investors.
Use your real name
By signing up, you indicate that you agree to the BiggerPockets Terms & Conditions.
The community here is like my own little personal real estate army that I can depend upon to help me through ANY problems I come across.
General Landlording & Rental Properties
All Forum Categories
Followed Discussions
Followed Categories
Followed People
Followed Locations
Market News & Data
General Info
Real Estate Strategies
Landlording & Rental Properties
Real Estate Professionals
Financial, Tax, & Legal
Real Estate Classifieds
Reviews & Feedback

Updated over 4 years ago on . Most recent reply

User Stats

414
Posts
38
Votes
Sami Gren
  • Rental Property Investor
  • new jersey
38
Votes |
414
Posts

"220 GFCI outlet " is there such a thing?

Sami Gren
  • Rental Property Investor
  • new jersey
Posted

Hi, 

I was wondering if there is such a thing as a 220 GFCI outlet?

I have an electric oven within 6 feet of a sink and (from attached picture) it's not GFCI

Most Popular Reply

Account Closed
  • Specialist
  • OverTheRainbow
909
Votes |
607
Posts
Account Closed
  • Specialist
  • OverTheRainbow
Replied
Originally posted by @Sami Gren:
Originally posted by @Kenneth Garrett:

@Sami Gren

The 220 outlet is a dedicated outlet not a duplex outlet and it doesn’t serve a countertop space.  It is not required to GFCI protected.

I looked it up and from my understanding it says that every countertop outlet OR anything within 6 feet must be GFCI?!

 I just had a fix & flip rewired from top to bottom (it was old aluminum wire) and had copper put in. I heard nothing about 220 GFCI. I didn't see it in NEC 2017. You may be thinking 20 amp circuits. As stated above, stoves, dryers, hot water heaters are dedicated. The new NEC 2020 is out and it states (note that it is for "locations that are supplied by single-phase branch circuits rated 150 volts or less to ground are required to have GFCI protection for personnel

You have to check and see if your city/state require NEC 2017 or NEC 2020 or neither (like Phoenix AZ)  but it's good to follow the code anyway.

2020 Edition: Section 210.8

Dwelling Units 210.8(A)

All 125- through 250-volt receptacles in the following locations that are supplied by single-phase branch circuits rated 150 volts or less to ground are required to have GFCI protection for personnel.

Bathrooms 210.8(A)(1)
Garages and accessory buildings 210.8(A)(2)
Outdoors 210.8(A)(3)
Crawl Spaces 210.8(A)(4)
Basements (finished and unfinished) 210.8(A)(5)
Kitchens 210.8(A)(6)
Sinks 210.8(A)(7)
Boathouses 210.8(A)(8)
Bathtubs or shower stalls 210.8(A)(9)
Laundry Areas 210.8(A)(10)
Indoor damp and wet locations 210.8(A)(11)
Boat Hoist 555.9

Other Than Dwelling Units 210.8(B)

All 125-volt through 250-volt receptacles supplied by single-phase branch circuits rated 150 volts or less to ground, 50 amperes or less, and all receptacles supplied by three-phase branch circuits rated 150 volts or less to ground, 100 amperes or less, installed in the following locations are required to have GFCI protection for personnel.

Bathrooms 210.8(B)(1)
Kitchens or areas with sink and permanent provisions forfood preparation or cooking 210.8(B)(2)
Rooftops 210.8(B)(3)
Outdoors 210.8(B)(4)
Sinks 210.8(B)(5)
Indoor damp and wet locations 210.8(B)(6)
Locker rooms w/shower facilities 210.8(B)(7)
Garages and accessory buildings 210.8(B)(8)
Crawl spaces — at or below grade 210.8(B)(9)
Unfinished areas of basements 210.8(B)(10)
Laundry areas 210.8(B)(11)
Bathtubs and shower stalls 210.8(B)(12)

Both Dwelling and Other Than Dwelling Units

Crawl Space Lighting Outlets 210.8(C)
Specific Appliances 210.8(D)
Equipment Requiring Servicing 210.8(E) [210.63)
Outdoor Outlets 210.8(F)
Sump Pumps 422.5(A)(6)
Dishwashers 422.5(A)(7)
Swimming Pools and Similar Inst. See Article 680

* Other GFCI requirements scattered throughout the NEC.