Skip to content
×
Try PRO Free Today!
BiggerPockets Pro offers you a comprehensive suite of tools and resources
Market and Deal Finder Tools
Deal Analysis Calculators
Property Management Software
Exclusive discounts to Home Depot, RentRedi, and more
$0
7 days free
$828/yr or $69/mo when billed monthly.
$390/yr or $32.5/mo when billed annually.
7 days free. Cancel anytime.
Already a Pro Member? Sign in here

Join Over 3 Million Real Estate Investors

Create a free BiggerPockets account to comment, participate, and connect with over 3 million real estate investors.
Use your real name
By signing up, you indicate that you agree to the BiggerPockets Terms & Conditions.
The community here is like my own little personal real estate army that I can depend upon to help me through ANY problems I come across.
Rehabbing & House Flipping
All Forum Categories
Followed Discussions
Followed Categories
Followed People
Followed Locations
Market News & Data
General Info
Real Estate Strategies
Landlording & Rental Properties
Real Estate Professionals
Financial, Tax, & Legal
Real Estate Classifieds
Reviews & Feedback

Updated over 9 years ago on . Most recent reply

User Stats

58
Posts
5
Votes
Brad Smith
  • Rental Property Investor
  • New Braunfels, TX
5
Votes |
58
Posts

Two wire house... again

Brad Smith
  • Rental Property Investor
  • New Braunfels, TX
Posted

Just read this:

Sec. 210-7(d)(3) permits any of the following installations when replacing a 2-wire ungrounded receptacle:

(a) Replace it with another 2-wire receptacle;

(b) Replace it with a GFCI-type receptacle and mark the receptacle with the words “No Equipment Ground;” or

(c) Replace it with a grounding-type receptacle protected by a GFCI device (circuit breaker or receptacle). Since the grounding terminals for the receptacles are not grounded, you must mark the receptacles with the words “GFCI Protected” and “No Equipment Ground

What about the face plates if they aren't GFCI's, do they need to be two prong? 

Do you put these "No Equipment Ground" labels on your receptacles?

Most Popular Reply

User Stats

13,450
Posts
8,349
Votes
Steve Babiak
  • Real Estate Investor
  • Audubon, PA
8,349
Votes |
13,450
Posts
Steve Babiak
  • Real Estate Investor
  • Audubon, PA
Replied
Originally posted by @Don Meinke:

...

That being said back to original post, subject,  how do you wire a gfi outlet into a 2 wire system and make it trip if there is a ground fault issue???  Do you HAVE to string a new bare wire from the box? Or is that just preferable if possible?

...

Ah, you have been exposed to the myth that a GFCI must have a ground wire in order to function as a ground fault protection device. That is a myth. The GFCI functions by sensing the amount of current in the hot and the amount of current in the neutral, and if those two currents do not match to within some small difference a ground fault is "declared" and the device trips - the ground current is not measured, it is assumed to be the difference between hot and neutral currents. As such, GFCIs are allowed by code to be ungrounded if properly labelled as such; appropriate labels are often found inside the packaging with the GFCI. 

And you can test that if you choose by disconnecting temporarily the ground wire from a GFCI and pushing the test button, and it should trip. 

Now, there are GFCI testers that are inserted into a receptacle to test the GFCI; if the GFCI is ungrounded, those testers will not trip the GFCI. Some would conclude from that that the GFCI is not protecting from ground faults, but pressing the test button on the GFCI is the only reliable test method. 