Skip to content
×
Try PRO Free Today!
BiggerPockets Pro offers you a comprehensive suite of tools and resources
Market and Deal Finder Tools
Deal Analysis Calculators
Property Management Software
Exclusive discounts to Home Depot, RentRedi, and more
$0
7 days free
$828/yr or $69/mo when billed monthly.
$390/yr or $32.5/mo when billed annually.
7 days free. Cancel anytime.
Already a Pro Member? Sign in here

Join Over 3 Million Real Estate Investors

Create a free BiggerPockets account to comment, participate, and connect with over 3 million real estate investors.
Use your real name
By signing up, you indicate that you agree to the BiggerPockets Terms & Conditions.
The community here is like my own little personal real estate army that I can depend upon to help me through ANY problems I come across.
General Landlording & Rental Properties
All Forum Categories
Followed Discussions
Followed Categories
Followed People
Followed Locations
Market News & Data
General Info
Real Estate Strategies
Landlording & Rental Properties
Real Estate Professionals
Financial, Tax, & Legal
Real Estate Classifieds
Reviews & Feedback

Updated about 4 years ago on . Most recent reply

User Stats

19
Posts
3
Votes
Belinda M.
3
Votes |
19
Posts

Do I need to update the rental current to code?

Belinda M.
Posted

I have a condo that was built in 1987. My current tenant is complaining that the circuit breaker trips when they use the Microwave and toaster at the same time in the kitchen.  I had an electrician check and the circuit is overloaded when they use the two appliances at the same time.  The recommendation from the electrician  is to update to have dedicated circuit for microwave and an extra circuit.  Also, since the circuit breaker panel can only handle so much and that too, he recommends to be updated.  This circuits and breaker panel updates will cost me around $5k-6k.   I would assume that when the condo was built in 1987, it was built up to code, could I leave the condo as it is and just recommend to the tenant to distribute the load of appliances in the kitchen.  Is that acceptable?   Thanks.  
 

Most Popular Reply

User Stats

31
Posts
7
Votes
Replied

Belinda,

If you had it inspected and there are no faults with wiring or a bad breaker then you need to do some math and see what the issue really is. 
Watts

The microwave and toaster both are high loads. Microwaves can pull 1300 watts and toaster could be anything from 400-600 watts. 

What is the amperage of the breaker they are on? Here’s an example.

A 15 amp breaker can supply a max of 1800 watts. 120volts x 15 amps. 

If the toaster uses 600 and the microwave 1300 then they are overloading the circuit (1900 watts) and the breaker is doing it’s job. 

So you could spend that $5-6k and end up with them still having the same issue. You could upgrade that circuit to a 20amp breaker but your wiring probably isn’t thick enough to carry the extra power without fire risk. 

So....

No. I’d tell them they are overloading a circuit and need to use the appliances separately or move the toaster to a different circuit. 